Forum

delta vfd fault cod...
 
Share:
Notifications
Clear all

delta vfd fault codes ou

1 Posts
1 Users
0 Reactions
314 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

The "OU" or Overvoltage Fault in a Delta VFD (Variable Frequency Drive) typically indicates that the DC bus voltage has exceeded the drive’s allowable limit

Common Causes of OU Fault:

  1. Regenerative Braking: When the motor decelerates too quickly, it acts like a generator and pushes voltage back into the drive

  2. Deceleration Time Too Short: A short deceleration time setting causes the motor to regenerate too much energy too quickly.

  3. Improper Braking Setup: No braking resistor or braking unit installed when needed. Braking resistor is too small or faulty.

  4. Power Supply Issues: Input voltage spikes or surges. Bad power quality (e.g., voltage imbalance or harmonics).

Troubleshooting Steps:

  1. Increase Deceleration Time: Adjust parameter For Deceleration Time.

  2. Install or Check Braking Resistor: Ensure a braking resistor is installed and properly sized. Check connections and condition of the resistor.

  3. Add a Braking Unit (If Needed): Required for larger drives or frequent/fast deceleration cycles.

  4. Use a Line Reactor or Surge Protector: Helps mitigate power line surges and voltage spikes.

  5. Check for Sudden Load Changes: Rapid load reduction can cause regenerative energy to surge back into the drive.

  6. Monitor Input Voltage: Use a multimeter or data logger to detect input surges or imbalance.