Ground fault in delta drive
Cause : Ground fault comes when that electrical current unintentionally flows from a phase conductor to the ground. This is typically due to insulation failure, improper wiring, or other faults in the motor, cabling, or drive itself.
"Ground fault" in "delta drive" indicate there is an unwanted electrical connection between a live conductor and the earth ground. This means drive will detect this abnormal current flow and trigger a fault to protect the system.
Common Causes of Ground Faults:
  1. Damaged Cables: Insulation breakdown in the power supply or motor cables can lead to an earth fault.
  2. Contamination: Dirt, moisture, or other contaminants can cause a conductive path between a live conductor and ground.
  3. Internal Drive Faults: Faulty components within the drive itself can create an earth fault.
  4. Grounding Issues: Inadequate or faulty grounding can contribute to earth faults.
  1. Inspect Cables: Visually inspect the power supply and motor cables for any signs of damage, such as cuts, abrasions, or insulation breakdown.
  2. Check for Contamination: Look for signs of dirt, moisture, or other contaminants on the cables or drive terminals.
  3. Use a Continuity Tester: Use a continuity tester to check for a connection between the live conductors and ground.
  4. Measure Insulation Resistance: Use an insulation tester to measure the insulation resistance of the cables. A low resistance indicates a potential earth fault.
  5. Check Grounding: Verify that the drive is properly grounded and that the grounding system is in good condition.
  6. Inspect Drive for Faults: Check the drive for any error codes or diagnostic indicators that might point to an earth fault.