Cause : IGBT overload comes when an IGBT within the drive's power electronics exceeds its rated current or power capacity. This overload can occur due to excessive current, heat, or switching frequency, which stresses the IGBT module beyond its safe operating limits.

IGBT overload fault in delta drive indicate that the Insulated Gate Bipolar Transistor (IGBT) module, which controls the switching of power to the motor, is being overloaded.

Potential Causes of IGBT Overload Fault:

  1. Excessive Motor Load:

    • The motor may be subjected to an excessively high load, which forces the IGBT to switch more current than it is rated for, causing an overload.
  2. High Switching Frequency:

    • Increasing the switching frequency of the IGBT can lead to higher power dissipation and excessive heat generation, which may trigger an overload fault.
  3. High Ambient Temperature:

    • If the drive is located in a high-temperature environment or has inadequate ventilation, the IGBT module can overheat, causing an overload condition.
  4. Drive Overcurrent:

    • Overcurrent conditions in the drive, such as a short circuit or phase-to-phase fault in the motor, can cause the IGBT to handle higher-than-rated current, leading to overload.
  5. Cooling Fan Failure:

    • If the drive’s cooling system (fans or heat sinks) is not functioning correctly, the IGBT module may overheat, triggering an overload fault.
  6. IGBT Damage or Deterioration:

    • Over time, IGBT modules may degrade or become damaged due to repeated thermal cycling, leading to higher electrical resistance and eventual overload.
  7. Voltage Spikes or Power Supply Issues:

    • Sudden voltage spikes or transients in the power supply can cause the IGBT module to experience excessive current, leading to an overload fault.
  8. Incorrect Drive Settings:

    • Incorrect drive settings, such as a misconfigured switching frequency or improper current limits, may cause excessive stress on the IGBT.

Troubleshooting Steps for IGBT Overload Fault:

  1. Check Motor Load:

    • Inspect the mechanical load on the motor. If the motor is subjected to excessive load, reduce the load or address any mechanical issues (e.g., jammed equipment or binding).
  2. Monitor Drive Current:

    • Use the drive’s diagnostic tools to monitor the current being supplied to the motor. Ensure that the motor is not drawing more current than the drive and IGBT are rated to handle.
    • If overcurrent is detected, inspect the motor for issues such as winding short circuits.
  3. Adjust Switching Frequency:

    • Check the drive’s switching frequency settings. If the frequency is set too high, reduce it to decrease the power dissipation in the IGBT module.
    • Use the manufacturer’s recommended switching frequency for your specific application and motor size.
  4. Inspect the Cooling System:

    • Ensure the cooling fans in the drive are functioning properly. Clean or replace any clogged or faulty fans.
    • Check the heat sinks for dust or dirt buildup and clean them if necessary to improve heat dissipation.
  5. Check Ambient Temperature:

    • Verify that the ambient temperature around the drive is within the recommended range. Improve ventilation or add external cooling systems if necessary to maintain the temperature within safe limits.
  6. Inspect Power Supply:

    • Ensure that the power supply to the drive is stable and free from voltage spikes. Consider installing surge protectors or filters to protect the drive from power transients.
  7. Test the IGBT Module:

    • If the fault persists, the IGBT module itself may be damaged or deteriorating. Inspect or test the IGBT for any signs of degradation, such as increased electrical resistance or heating. If necessary, replace the IGBT module.