Forum

oL fault in delta d...
 
Share:
Notifications
Clear all

oL fault in delta drive

1 Posts
1 Users
0 Reactions
45 Views
Posts: 17563
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Over load comes when the motor is drawing excessive current exceeding the drive's capacity for a sustained period.

The ol fault in delta drive indicates an overload condition. This means the drive detects that the output current exceeds its safe operating limit for a certain duration.

  1. Reduce the load.
  2. Increase the setting value for (accel./decel. time).
  3. Replace the drive with a larger capacity model.
  4. Check the status of three-phase motor.
  5. Check if the cable is broken or the screws are loose.
Share: