ot2 fault in delta drive

1 Posts
1 Users
0 Reactions
59 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over torque 2 comes when the motor connected to the drive has exceeded the set torque limit for a certain period.

The ot1 fault in delta drive indicates an over-torque condition. This means the output current exceeds the over-torque detection level and exceeds over-torque detection time.

  1. Reduce the load.
  2. Replace the motor with a larger capacity model.
  3. Increase the setting values for (accel./decel. time).
  4. Adjust the torque compensation until the current reduces and the motor does no stall.