How can resolve problem AnL ACI analog signal loss Warning in delta ME300 series Drive ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog input current loss (including all analog 4–20 mA signals)

Loose or broken ACI wiring

Tighten the terminals again.
Replace with a new cable.

Replace with a new device.

If the AnL error still occurs after checking all the wiring.

Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warning treatment parameter

Pr.03-19
0: Disable

1: Continue operation at the last frequency (warning, the keypad displays ”AnL”)

2: Decelerate to 0 Hz (warning, the keypad displays ”AnL”)

3: Stop immediately and display “ACE”