EoL1 Electronic thermal relay 1 protection fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
472 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem EoL1 Electronic thermal relay 1 protection fault in delta ME300 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Electronic thermal relay 1 protection. The drive coasts to stop once it activates.

The load is too large. Reduce the load.

Increase the setting values for Pr.01-12–01-19 (accel./decel. time)

Check motor data.

Incorrect value of electronic thermal relay : Reset to the correct motor rated current.

Reply