GFF Ground fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
241 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem GFF Ground fault in delta ME300 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : When (one of) the output terminal(s) is grounded, short
circuit current is larger than Pr.06-60 setting value, and
the detection time is longer than Pr.06-61 time setting,
GFF occurs.

NOTE: the short circuit protection is provided for AC
motor drive protection, not to protect you.

Check the motor insulation value with megger. Replace the motor if the insulation is poor.

Troubleshoot the short circuit.
Replace the cable.