How can resolve problem oL Overload fault in delta ME300 series drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The AC motor drive detects excessive drive output current.
Overload capacity:

Normal duty:

Sustains for one minute when the drive outputs 120% of the drive’s rated output current.
Sustains for three seconds when the drive outputs 150% of the drive’s rated output current.
Heavy duty:

Sustains for one minute when the drive outputs 150% of the drive’s rated output current.
Sustains for three seconds when the drive outputs 200% of the drive’s rated output current.

The load is too large. Reduce the load.

Increase the setting values for Pr.01-12–01-19 (accel. / decel. time).