How can resolve problem oL Overload fault in delta ME300 series drive ?
1 Reply
Apr 23, 2022 7:57 am
Cause : The AC motor drive detects excessive drive output current.
Overload capacity:
Normal duty:
Sustains for one minute when the drive outputs 120% of the drive’s rated output current. Sustains for three seconds when the drive outputs 150% of the drive’s rated output current.
Heavy duty:
Sustains for one minute when the drive outputs 150% of the drive’s rated output current. Sustains for three seconds when the drive outputs 200% of the drive’s rated output current.
The load is too large. Reduce the load.
Increase the setting values for Pr.01-12–01-19 (accel. / decel. time).