oPL1 Output phase loss U phase fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
540 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oPL1 Output phase loss U phase fault in delta ME300 series drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : U phase output phase loss.

Check the cable and replace it if necessary.
Check the motor’s internal wiring. If the fault still exists, replace the motor.

Check motor cable, if fault coming after this check drive hardware.

Fault treatment parameter

Pr.06-45
0: Warn and continue operation
1: Fault and ramp to stop
2: Fault and coast to stop
3: No warning

 

Reply