How can resolve problem oPL3 Output phase loss W phase fault in delta ME300 series drive ?
1 Reply
Apr 25, 2022 5:44 am
Cause : W phase output phase loss.
Check the cable and replace it if necessary.
Check the motor’s internal wiring. If the fault still exists, replace the motor.
Check motor cable and drive hardware.
Fault treatment parameter
Pr.06-45
0: Warn and continue operation
1: Fault and ramp to stop
2: Fault and coast to stop
3: No warning