ot1 Over-torque 1 fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
548 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ot1 Over-torque 1 fault in delta ME300 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : When output current exceeds the over-torque detection level (Pr.06-07) and exceeds over-torque detection time (Pr.06-08), and when Pr.06-06 or Pr.06-09 is set to 2 or 4, the ot1 error displays.

Incorrect parameter setting

Reset Pr.06-07 and 06-08.

Correct the parameter settings for speed tracking.
1. Start the speed tracking function.

2. Adjust the maximum current for Pr.07-09 speed tracking.