How can resolve problem ot1 Over-torque 1 Warning in delta ME300 series Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over-torque 1 warning.

Incorrect parameter setting

Configure the settings for Pr.06-07 and Pr.06-08 again.

The load is too large.

- Decrease the loading.
- Replace with a motor with larger capacity.

Warning treatment parameter

Pr.06-06 = 1 or 3
0: No function

1: Continue operation after over-torque detection during constant speed
operation

2: Stop after over-torque detection during constant speed operation

3: Continue operation after over-torque detection during RUN

4: Stop after over-torque detection during RUN