How can resolve problem uC Under current fault in delta ME300 series drive ?
1 Reply
Apr 25, 2022 5:12 am
Cause : Low current detection.
Check the load status.
Check if the motor capacity matches the load.
Check motor rating if small motor connected to drive then this fault coming.
Fault treatment parameter
Pr.06-73
0: No function
1: Fault and coast to stop
2: Fault and ramp to stop by the second deceleration time
3: Warn and continue operation