Forum

Share:
Notifications
Clear all

uC Under current fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
452 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem uC Under current fault in delta ME300 series drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Low current detection.

Check the load status.
Check if the motor capacity matches the load.

Check motor rating if small motor connected to drive then this fault coming.

Fault treatment parameter

Pr.06-73
0: No function

1: Fault and coast to stop

2: Fault and ramp to stop by the second deceleration time

3: Warn and continue operation

Reply
Share: