Forum

Share:
Notifications
Clear all

uC Under current Warning in delta ME300 series Drive

2 Posts
1 Users
0 Reactions
452 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem uC Under current Warning in delta ME300 series Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Low current.

Exclude the connection issue of the motor and its load.

Set the proper settings for Pr.06-71, Pr.06-72 and Pr.06-73.

Check the loading status.
Make sure the loading matches the motor capacity.

Warning treatment parameter

Pr.06-73
0: No function

1: Fault and coast to stop

2: Fault and ramp to stop by second deceleration time

3: Warn and continue operation

Reply
Share: