ocA fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
1,168 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ocA fault in delta MH300 drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-current during acceleration (ocA)

Output current exceeds 3 times of the rated current during acceleration. When ocA occurs, the drive closes the gate of the output immediately, the motor runs freely, and the display shows an ocA error.

Acceleration time is too short.

1. Increase the acceleration time
2. Increase the acceleration time of S-curve

3. Set auto-acceleration and auto-deceleration parameter (Pr.01-44)

4. Set over-current stall prevention function (Pr.06-03)

5. Replace the drive with a larger capacity model.

The load is too large - Check if the output current during the whole working process exceeds the AC motor drive’s rated current. If yes, replace the AC motor drive with a
larger capacity model.

The ocA occurs due to short circuit or ground fault at the output side of the drive.
Check for possible short circuits between terminals with the electric meter:

B1 corresponds to U, V, W; DC - corresponds to U, V, W;
corresponds
to U, V, W.