Forum

Share:
Notifications
Clear all

ocn fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
349 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ocn fault in delta MH300 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-current during steady operation (ocn)

Output current exceeds 3 times of the rated current during constant speed. When ocn occurs, the drive closes the gate of the output immediately, the motor runs freely, and the display shows an ocn error.

Short-circuit at motor output due to poor insulation wiring - Without considering the short circuits, check the motor cable or replace the cable before turning on the power.

The ocn occurs due to short circuit or ground fault at the output side of the drive.
Check for possible short circuits between terminals with the electric meter:
B1 corresponds to U, V, W; DC- corresponds to U, V, W; corresponds to U, V, W.

Reply
Share: