Forum

Share:
Notifications
Clear all

oH3 fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
238 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oH3 fault in delta MH300 drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Motor overheating (oH3)

The load is too large -

Reduce the load.
Increase the motor capacity.

Fault treatment parameter

Pr.06-29
0: Warn and continue operation

1: Fault and ramp to stop

2: Fault and coast to stop

3: No warning

Ambient temperature is too high -

Change the installed place if there are heating devices in the
surroundings.

Install/ add cooling fan or air conditioner to lower the ambient
temperature.

 

 

Reply
Share: