oPL2 fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
695 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oPL2 fault in delta MH300 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Output phase loss V phase (oPL2)

V phase output phase loss

Check the cable and replace it if necessary.
Check the motor’s internal wiring. If the fault still exists, replace the motor.

Check if the control board cable is loose. If yes, reconnect the cable and
run the drive to test. If the fault still exists, return to the factory for repair.

Check if the three-phase current is balanced with a current clamp meter.

Fault treatment parameter

Pr.06-45
0: Warn and continue operation

1: Warn and ramp to stop

2: Warn and coast to stop

3: No warning

Check drive IGBT using multimeter & IGBT driving circuit using multimeter.

Reply