Forum

Share:
Notifications
Clear all

ovA fault in delta MH300 drive

2 Posts
1 Users
0 Reactions
372 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ovA fault in delta MH300 drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-voltage during acceleration (ovA)

DC bus over-voltage during acceleration.When ovA occurs, the drive closes the gate of the output, the motor runs freely, and the display show s an ovA error.

Reset condition - Reset only when DC bus voltage is lower than 90% of the over-voltage level.

Decrease the acceleration time.
Use brake unit or DC bus.

Replace the drive with a larger capacity model
.

Acceleration time is too short

Check if the over-voltage warning occurs after acceleration stops.
When the warning occurs, do the following:

1. Increase the acceleration time

2. Set Pr.06-01 over-voltage stall prevention

3. Increase the setting value for Pr.01-25 S-curve acceleration arrival
time 2

 

Reply
Share: