ovd fault in delta MH300 drive
How can resolve problem ovd fault in delta MH300 drive ?
Over-voltage during deceleration (ovd)
DC bus over-voltage during deceleration.When ovd occurs, the drive closes the gate of the output, the motor runs freely, and the display shows an ovd error.
Deceleration time is too short, causing too large regenerative energy of the load
1. Increase the setting value for Pr.01-13, Pr.01-15, Pr.01-17 and
Pr.01-19 (deceleration time).
2. Connect brake resistor, brake unit or DC bus to the drive.
3. Reduce the brake frequency.
4. Replace the drive with a larger capacity model.
5. Use S-curve acceleration/deceleration.
6. Use over-voltage stall prevention (Pr.06-01).
7. Use auto-acceleration and auto-deceleration (Pr.01-44).
Adjust braking level (Pr.07-01 or the bolt position of the brake unit)
Check the wiring of brake resistor or brake unit.