Delta MS300 Series Drive
1
Posts
1
Users
0
Reactions
149
Views
Jun 22, 2024 10:37 am
Cause : CANopen index setting exceed limit comes when you update the firmware version of the control board, the FRAM internal data does not change, then CFrE fault occurs. This means CANopen internal memory error.
- Disable CANopen (Pr.09-36=0).
- Reset CANopen (Pr.00-02=7).
- Reset CANopen station address (Pr.09-36).