How can resolve problem coc fault in delta MS300 drive ?

1 Reply
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

W-phase over-current before run

W-phase short circuit detected when the output wiring
detection is performed before the drive runs.

Check if the motor’s internal wiring and the UVW wiring of the drive output
terminal are correct.

The coc occurs due to the short circuit or ground fault at the output side of the
drive. Check for possible short circuits between terminals with the electric meter:
B1 corresponds to U, V and W; DC- corresponds to U, V and W;
corresponds to U, V and W

Check drive IGBT using multimeter.