Delta MS300 Series Drive
1
Posts
1
Users
0
Reactions
364
Views
Jun 22, 2024 6:45 am
Cause : Over-current during steady operation comes when the current flowing from the drive to the motor has exceeded the set limit while the motor is running at a constant speed.
The ocn error code on your Delta MS300 drive indicates an Over-current During Steady State Operation condition. This means the current flowing from the drive to the motor has exceeded the set limit while the motor is running at a constant speed.
- Check the motor cable and remove causes of the short circuits, or replace the cable before turning on the power.
- Check the motor insulation value with megger. Replace the motor if the insulation is poor.
- Increase the AC motor drive’s capacity.
- Reduce the load or increase the capacity of AC motor drive.