How can resolve problem oL fault in delta MS300 drive ?
1 Reply
Apr 26, 2022 7:19 am
Over load
The AC motor drive detects excessive drive output
current.
Overload capacity:
Normal duty:
Sustains for one minute when the drive outputs
120% of the driveβs rated output current.
Sustains for three seconds when the drive outputs
150% of the driveβs rated output current.
Heavy duty:
Sustains for one minute when the drive outputs
150% of the driveβs rated output current.
Sustains for three seconds when the drive outputs
200% of the driveβs rated output current.
Reduce the load during low-speed operation.
Increase the drive capacity.