Forum

Share:
Notifications
Clear all

oL fault in delta MS300 drive

2 Posts
1 Users
0 Reactions
534 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oL fault in delta MS300 drive ?

Topic Tags
1 Reply
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Over load

The AC motor drive detects excessive drive output
current.
Overload capacity:
Normal duty:
Sustains for one minute when the drive outputs
120% of the drive’s rated output current.
Sustains for three seconds when the drive outputs
150% of the drive’s rated output current.

Heavy duty:
Sustains for one minute when the drive outputs
150% of the drive’s rated output current.
Sustains for three seconds when the drive outputs
200% of the drive’s rated output current.

Reduce the load during low-speed operation.
Increase the drive capacity.

 

Reply
Share: