How can resolve problem ovA fault in delta MS300 drive ?
1 Reply
Apr 26, 2022 7:04 am
Over-voltage during acceleration
DC bus over-voltage during acceleration.
When ovA occurs, the drive closes the gate of the
output, the motor runs freely, and the display shows an
ovA error
Decrease the acceleration time
Use a braking unit or DC bus
Replace the drive with a larger capacity model
Check if the input voltage is within the rated AC motor drive input voltage range,
and check for possible voltage spikes.
Use a braking unit or DC bus.