ovn fault in delta MS300 drive
How can resolve problem ovn fault in delta MS300 drive ?
Over-voltage during constant speed
DC bus over-voltage at constant speed.
When ovn occurs, the drive closes the gate of the
output immediately, the motor runs freely, and the
display shows an ovn error.
1. Connect the brake resistor, braking unit or DC bus to the drive.
2. Reduce the load.
3. Replace the drive with a larger capacity model.
4. Adjust the braking level (Pr.07-01 or bolt position of the brake unit
Check the wiring of the brake resistor or braking unit.