Forum

Share:
Notifications
Clear all

PGF2 fault delta ms300 drive

1 Posts
1 Users
0 Reactions
115 Views
Posts: 18015
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : PG feedback loss comes when incorrect setting of encoder parameter or incorrect selection of the control mode.

PGF2 fault delta ms300 drive indicate PG feedback loss. This means the VFD is unable to receive feedback from the Pulse Generator (PG) or encoder. This feedback is crucial for the VFD to accurately control the motor speed and position.

  1. Reset encoder parameters (Pr.10-00 and Pr.10-02).
  2. Choose the correct control mode.
Share: