PHL Phase loss warning in delta MS300 drive

2 Posts
1 Users
0 Reactions
385 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem PHL Phase loss warning in delta MS300 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Phase loss (PHL)

Input phase loss warning. Phase loss of the input power - Verify the wiring of the main circuit.

If the power of main circuit works well, check if the MC of the main circuit is
broken.
Cycle the power after verifying the power is normal.

If supply is ok then check rectifier using multimeter.

 

Reply