How can resolve problem PID warning in delta MS300 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

PID feedback error (PID)

PID feedback loss (warning for analog feedback signal; works only when PID enables)

When the analog input is lower than 4 mA (only detects analog input 4–20 mA)

Warning” occurs when Pr.08-09=0 or 3. The “Warning” automatically
clears when the feedback signal is larger than 4 mA.

“Error” occurs when Pr.08-09=1 or 2. You must reset manually.

Warning setting parameter

Pr.08-09
0: Warn and continue operation
1: Fault and ramp to stop
2: Fault and coast to stop
3: Warn and operate at last frequency