Delta MS300 Series Drive
2
Posts
1
Users
0
Reactions
614
Views
Apr 26, 2022 6:43 am
How can resolve problem PLor warning in delta MS300 drive ?
1 Reply
Apr 26, 2022 6:44 am
PLC buffer overflow (PLor)
PLC register overflow - When PLC runs the last command and the command exceeds the maximum capacity of the program, then PLor warning occurs.
The program detects internal source code error during PLC operation
1. Disable PLC
2. Reset the PLC program (Pr.00-02=6)
3. Enable PLC
4. Re-download the PLC program