How can resolve problem PLSn warning in delta MS300 drive ?

1 Reply
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Checksum error (PLSn)

PLC checksum error - PLC checksum error is detected after the drive is powered on, then PLSn warning occurs.

The program detects checksum error during PLC operation - 1. Disable PLC
2. Reset the PLC program (Pr.00-02=6)
3. Enable PLC
4. Re-download the PLC program