How can resolve problem PLSn warning in delta MS300 drive ?
1 Reply
Apr 26, 2022 6:47 am
Checksum error (PLSn)
PLC checksum error - PLC checksum error is detected after the drive is powered on, then PLSn warning occurs.
The program detects checksum error during PLC operation - 1. Disable PLC
2. Reset the PLC program (Pr.00-02=6)
3. Enable PLC
4. Re-download the PLC program