AL061 alarm in delta servo drive indicates Encoder under voltage. This means the voltage of the absolute encoder is lower than the specification.
- Check if the voltage of the battery on the panel is lower than 3.1V (tentative specification).
- Measure if the voltage of the battery is lower than 3.1V (tentative specification).