AL07A alarm in delta ASDA-A2 servo drive indicates Loss of encoder Z pulse. This means feedback loss of encoder z pulse due to loose connection or faulty encoder.
  1. Check if the motor is well grounded.
  2. Check if the encoder cable is separated from the power supply or any high-current cable to avoid interference.
  3. Check if the encoder uses shielded cable.