How can resolve problem oL1 fault in delta VFD-B series drive ?
1 Reply
May 17, 2022 12:48 pm
Overload 1 Internal electronic overload trip
1. Check for possible motor overload.
2. Check electronic thermal overload setting.
3. Use a higher power motor.
4. Reduce the current level so that the drive
output current does not exceed the value set
by the Motor Rated Current Pr.7-00.
Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.