How can resolve problem cE fault in delta VFD E series drive ?
Topic Tags
1 Reply
Admin
Topic starter
(@click2electro)
Member
Communication Fault
1. Check the RS485 connection between the AC
motor drive and RS485 master for loose wires
and wiring to correct pins.
2. Check if the communication protocol, address,
transmission speed, etc. are properly set.
3. Use the correct checksum calculation.
4. Please refer to group 9 in the chapter 5 for
detail information.
Reply