oc Over current fault in delta VFD E series drive
How can resolve problem oc Over current fault in delta VFD E series drive ?
Topic Tags
Over current
Abnormal increase in current.
1. Check if motor power corresponds with the
AC motor drive output power.
2. Check the wiring connections to U/T1, V/T2,
W/T3 for possible short circuits.
3. Check the wiring connections between the AC
motor drive and motor for possible short
circuits, also to ground.
4. Check for loose contacts between AC motor
drive and motor.
5. Increase the Acceleration Time.
6. Check for possible excessive loading
conditions at the motor.
7. If there are still any abnormal conditions when
operating the AC motor drive after a short-
circuit is removed and the other points above
are checked,
Check drive IGBT using multimeter.