Forum

Share:
Notifications
Clear all

ocA fault in delta VFD E series drive

2 Posts
1 Users
0 Reactions
510 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem ocA fault in delta VFD E series drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-current during acceleration

1. Short-circuit at motor output: Check for
possible poor insulation at the output lines.
2. Torque boost too high: Decrease the torque
compensation setting in Pr.07.02.
3. Acceleration Time too short: Increase the
Acceleration Time.
4. AC motor drive output power is too small:
Replace the AC motor drive with the next
higher power model.

Reply
Share: