Lv Low voltage fault in delta VFD EL series drive

2 Posts
1 Users
0 Reactions
603 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem Lv Low voltage fault in delta VFD EL series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Low voltage

The AC motor drive detects that the DC bus voltage has fallen below its minimum value.

1. Check whether the input voltage falls within the AC
motor drive rated input voltage range.
2. Check for abnormal load in motor.
3. Check for correct wiring of input power to R-S-T (for 3-
phase models) without phase loss.

Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.