Forum

Share:
Notifications
Clear all

oL Overload fault in delta VFD EL series drive

2 Posts
1 Users
0 Reactions
467 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oL Overload fault in delta VFD EL series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Overload

The AC motor drive detects excessive drive output current.

NOTE: The AC motor drive can withstand up to 150% of the rated current for a maximum of 60 seconds.

1. Check whether the motor is overloaded.
2. Reduce torque compensation setting in Pr.07.02.
3. Use the next higher power AC motor drive model.

Reply
Share: