How can resolve problem oL Overload fault in delta VFD EL-W series drive ?

1 Reply
Posts: 14931
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Overload

The AC motor drive detects excessive drive output current.

NOTE: The AC motor drive can withstand up to 150% of the rated current for a maximum of 60 seconds.

1. Check whether the motor is overloaded.
2. Reduce the torque compensation setting (Pr.07.02).
3. Use the next higher power AC motor drive model.