Forum

Share:
Notifications
Clear all

oL1 fault in delta VFD-L series drive

2 Posts
1 Users
0 Likes
320 Views
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oL1 fault in delta VFD-L series drive ?

1 Reply
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Internal electronic overload trip

1. Check for possible motor overload.
2. Check electronic thermal overload
setting.
3. Increase motor capacity.
4. Reduce the current level so that the
drive output current does not exceed the
value set by the Motor Rated Current
Pr.7-00.

Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.

Reply
Share: