Forum

Share:
Notifications
Clear all

Lv fault in delta VFD-M series drive

2 Posts
1 Users
0 Reactions
363 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem Lv fault in delta VFD-M series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Low voltage

The AC motor drive detects that the DC bus voltage has fallen below its minimum value

1. Check whether the input voltage falls within the
AC motor drive rated input voltage range.
2. Check for abnormal load in motor.
3. Check for correct wiring of input power to R-S-T
(for 3-phase models) without phase loss

Reply
Share: