Delta VFD-M Series Drive
2
Posts
1
Users
0
Reactions
500
Views
May 16, 2022 11:46 am
How can resolve problem ocn fault in delta VFD-M series drive ?
1 Reply
May 16, 2022 11:47 am
Over-current during steady state operation:
1. Short-circuit at motor output.
2. Sudden increase in motor loading.
3. AC drive output capacity is too small.
1. Check for possible poor insulation at the output line.
2. Check for possible motor stall.
3. Replace with the AC drive with one that has a higher output capacity (next HP size).