Forum

Share:
Notifications
Clear all

oL1 fault in delta VFD-S series drive

2 Posts
1 Users
0 Reactions
773 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oL1 fault in delta VFD-S series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Overload 1

Internal electronic overload trip

1. Check for possible motor overload.
2. Check electronic thermal overload setting.
3. Use a higher power motor.
4. Reduce the current level so that the drive
output current does not exceed the value set
by the Motor Rated Current Pr.7-00.

Reply
Share: