Delta VFD-S Series Drive
2
Posts
1
Users
0
Reactions
773
Views
May 16, 2022 9:53 am
How can resolve problem oL1 fault in delta VFD-S series drive ?
1 Reply
May 16, 2022 9:54 am
Overload 1
Internal electronic overload trip
1. Check for possible motor overload.
2. Check electronic thermal overload setting.
3. Use a higher power motor.
4. Reduce the current level so that the drive
output current does not exceed the value set
by the Motor Rated Current Pr.7-00.