OL fault in delta VFD-V series drive

2 Posts
1 Users
0 Reactions
416 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem OL fault in delta VFD-V series drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

OL: AC drive overload
Output current exceeds the
AC drive-bearable current;
e.g. could sustain for 60
seconds if the output is
150% of the AC drive rated
current.

Decrease the loading and extend
the acceleration time
‹ Check whether the motor is
overloaded
‹ Decrease the (Pr. 07-02) torque
level-up setting
‹ Increase the AC drive output
capacity