How can resolve problem oH2 fault in delta VFD-VE series drive ?
1 Reply
May 16, 2022 5:29 am
Heatsink overheating
Heat sink temperature exceeds 90 o C
1. Ensure that the ambient temperature falls within the specified temperature range.
2. Make sure that the ventilation holes are not obstructed.
3. Remove any foreign objects from the heatsinks and check for possible dirty heat sink fins.
4. Check the fan and clean it.
5. Provide enough spacing for adequate ventilation.