Forum

Share:
Notifications
Clear all

Lvd DC bus voltage is lower fault in delta VJ series Drive

2 Posts
1 Users
0 Reactions
529 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem Lvd DC bus voltage is lower fault in delta VJ series Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DC bus voltage is lower than the setting in Pr02-07 during deceleration.

1. Check if the voltage of input power is
normal.
2. Check if there is any sudden heavy
load.
3. Adjust the low voltage level in
Pr02-07.

4. Lvn often occurs when the motor
drive has a power failure while the
operating signals are still being sent.

Reply