Drives
1
Posts
1
Users
0
Reactions
11
Views
Apr 28, 2025 12:53 am
Cause : Current limit comes when the output current exceeded the set current limit. The drive's control system is limiting the output to prevent the motor from exceeding a programmed torque value.
danfoss error 12 indicates a "Current limit" condition. This means the drive has detected that the motor's torque has exceeded a predefined limit set in the drive's parameters.
Troubleshooting Steps:
Follow these steps to resolve danfoss error 12 problem:
- If the motor torque limit is exceeded during ramp up, extend the ramp up time.
- If the generator torque limit is exceeded during ramp down, extend the ramp down time.
- If torque limit occurs while running, possibly increase the torque limit.
- Be sure the system can operate safely at a higher torque.
- Check the application for excessive current draw on the motor.