Cause : Motor phase loss comes when one of the three phases of power supply to a connected motor is interrupted or disconnected. his can cause imbalances in motor operation, leading to issues like overheating, reduced torque, or even motor damage.

"motor phase loss" fault in "drive" indicate that one of the three phases supplying power to the motor is either lost, disconnected, or not functioning correctly. This means drive unable to detect motor or the ration of motor is small as compare to drive.

Here are causes and troubleshooting steps for a motor phase loss fault:

Potential Causes:

  1. Wiring Issues:

    • Loose, disconnected, or broken wiring between the drive and motor can cause phase loss.
    • Check for any burnt or damaged wires.
  2. Blown Fuse or Breaker:

    • One phase might have a blown fuse or breaker tripped, causing the fault.
  3. Drive Malfunction:

    • The drive's internal components could be faulty, leading to a false detection of phase loss.
    • This could be related to the power supply or control circuitry.
  4. Motor Issues:

    • The motor windings could be damaged or one of the windings may be open.
  5. Improper Connections:

    • Check for improper or loose connections in the motor terminals or drive output.
  6. Power Supply Issues:

    • Inconsistent or unstable power supply to the drive might lead to phase loss detection.

Troubleshooting Steps:

  1. Check the Input Power:

    • Ensure that all three phases are present and stable.
    • Use a multimeter to check the voltage across all three phases at the drive input.
  2. Inspect the Motor and Drive Wiring:

    • Check for any loose or damaged wiring.
    • Make sure all connections between the drive and the motor are secure.
  3. Check the Fuses/Breakers:

    • Verify that all fuses are intact and breakers are not tripped.
  4. Test the Motor:

    • If you suspect the motor, test the motor windings using an insulation resistance tester (megger) or ohmmeter to check for open or short circuits.
  5. Examine the Drive Parameters:

    • Look into the drive's diagnostic information for any further error codes.
    • Reset the drive after ensuring all issues are resolved.